Re: BHF Series Replacement

Hi Mr.Thota, The replacement to the BHF62CT-100 package would be part numbers BHI62ST-100 for the geared motor and FRN0002C2S-7U for the VFD. The VFD we offer is a Fuji VFD. The dimensions and programming does change. I will link both below for your reference. https://catalog.orientalmotor.com/item/...
by om_tech_support_KR
Wed Oct 23, 2019 11:21 am
Forum: Servo Motors & Controls
Topic: Minimum wiring required between SCX11 and NXD75-s
Replies: 3
Views: 244

Re: Minimum wiring required between SCX11 and NXD75-s

Hi Mark,

The * in the manual means the outputs can be changed with the software but you are correct in that those aren't necessary to run the motor. From the input side if you don't have any torque limits set then you wouldn't need the TL, M0 and M1 inputs. Also P-REQ and P-Preset won't be necessary.
by om_tech_support_KR
Wed Oct 23, 2019 7:09 am
Forum: Servo Motors & Controls
Topic: Minimum wiring required between SCX11 and NXD75-s
Replies: 3
Views: 244

Re: Minimum wiring required between SCX11 and NXD75-s

Hi Mark, The I/O that will need to be wired from the CN7 I/O connector on the NXD75-S in torque control mode would be the CW and CCW, M0, M1, ALM-RST, and IN-COM for the inputs. For the outputs on the NX driver you would need the ASG, BSG, ZSG, ALM, READY and GND either pin 2 or 21 both GND pins are...
by om_tech_support_KR
Fri Oct 18, 2019 1:14 pm
Forum: Stepper Motors and Controls
Topic: I/O cable for AR Series, AC Input type Stepper Motor
Replies: 1
Views: 177

Re: I/O cable for AR Series, AC Input type Stepper Motor

Hi Mr.Thota, I will link below the 5 compatible I/O cables. 2 are straight type, 2 right angle type and 1 is a terminal block type. We offer the straight and right angle type in 1 and 2 meter lengths. The terminal block type is 1 meter. https://catalog.orientalmotor.com/group/accessories-32486/ard-c...
by om_tech_support_KR
Mon Oct 07, 2019 8:38 am
Forum: Servo Motors & Controls
Topic: Multiple NXM65A-PS10 control
Replies: 2
Views: 333

Re: Multiple NXM65A-PS10 control

Hi Markus,

Correct each motor will require its own driver and its own SCX11 controller since this is a single axis controller.
by om_tech_support_KR
Thu Oct 03, 2019 7:45 am
Forum: Stepper Motors and Controls
Topic: ETO Alarm Clear Using Alarm Reset
Replies: 2
Views: 440

Re: ETO Alarm Clear Using Alarm Reset

Hi Morrissette, Only the C-ON would have an effect with how the driver functions. If C-ON is set as one of the I/O then you would have to turn it on to provide current to the motor when ready to run after the ETO-Alarm is cleared. When its not set to the I/O then the current is always provided to th...
by om_tech_support_KR
Mon Sep 30, 2019 2:09 pm
Forum: Speed Control Systems
Topic: Fuji Modbus Setup
Replies: 0
Views: 318

Fuji Modbus Setup

Q: What parameters are necessary for Modbus control using a Fuji VFD. A: For the motor parameter setup you can reference the previous forum post linked below. https://www.orientalmotorforum.com/viewtopic.php?f=23&t=4351&p=8258&hilit=fuji#p8258 For the Modbus parameters they would be the ones listed ...
by om_tech_support_KR
Fri Sep 27, 2019 1:27 pm
Forum: Stepping Motors & Controls
Topic: Alpha Step AR serial driver and AS serial motor
Replies: 1
Views: 330

Re: Alpha Step AR serial driver and AS serial motor

Hi Hugh,

Unfortunately the AR drivers will not be compatible with the AS series motor. They will have to be replaced also.
by om_tech_support_KR
Thu Aug 22, 2019 12:46 pm
Forum: Stepper Motors and Controls
Topic: CVK Series, Radiation Protection
Replies: 2
Views: 459

Re: CVK Series, Radiation Protection

Hi Mr.Thota,

In regards to your inquiry unfortunately our products haven't been tested under these conditions. You would have to test them to verify if they will operate under these conditions.
by om_tech_support_KR
Tue Aug 13, 2019 6:34 am
Forum: Stepper Motors and Controls
Topic: CVK Series TIM & Alarm Output
Replies: 4
Views: 709

Re: CVK Series TIM & Alarm Output

Hi Mr.Thota,

From the wiring diagram the 24 VDC would go to pins 9 and 11. The pins 10 and 12 would go to 0 VDC. When using 24 VDC use a resistor 2.4 Kohm or larger to keep current at 10 mA or less.
by om_tech_support_KR
Tue Aug 06, 2019 11:23 am
Forum: Stepper Motors and Controls
Topic: CVK Series TIM & Alarm Output
Replies: 4
Views: 709

Re: CVK Series TIM & Alarm Output

Hi Mr.Thota, For the CVD228BR-K driver since they are open-collector type outputs you have to supply the 24 VDC voltage to the output to read that voltage when outputs are on. Reference page 8 of the link below for sample wiring diagram. You will have to use resistors to limit the current to less th...
by om_tech_support_KR
Tue Aug 06, 2019 11:13 am
Forum: Linear and Rotary Actuators and Controls
Topic: DRL Series Motorised Actuator
Replies: 1
Views: 586

Re: DRL Series Motorised Actuator

Hi Mr.Thota, The DRLII series is an open loop 5 phase motor so you will have to use a sensor for a defined home position. The DRS2 series would be a closed loop option with an absolute encoder as feedback but we don't offer one at the same frame size you were looking for. I will link them below for ...
by om_tech_support_KR
Wed Jul 24, 2019 8:31 am
Forum: Stepper Motors and Controls
Topic: Load with Stand while Power-off activated condition
Replies: 1
Views: 412

Re: Load with Stand while Power-off activated condition

Hi Mr.Thota,

The static friction torque given would be of the motor only without the gearhead. To get the total static friction torque of a geared motor you would multiply that value by the gear ratio. This would be the case for both of those electromagnetic brake motors.
by om_tech_support_KR
Mon Jul 22, 2019 1:37 pm
Forum: AC Motors
Topic: 2RK6RGN-CM encoder
Replies: 1
Views: 449

Re: 2RK6RGN-CM encoder

Hi Hawaiifairing,

The 2RK6RGN-CM feedback is tachogenerator not encoder. This speed control motor had a dedicated speed controller it will not be compatible with an Arduino.
by om_tech_support_KR
Thu Jul 18, 2019 1:27 pm
Forum: Stepper Motors and Controls
Topic: Unexplained exception for ReadWrite Multiple Registers (FC 17h)
Replies: 4
Views: 837

Re: Unexplained exception for ReadWrite Multiple Registers (FC 17h)

Hi dp1, After you get the exception do you get any alarms? Can you run the diagnosis function code 08h shown on page 270 to verify if getting the same response after you get the exception code. After you change register 1393h to 0 can you check in the MEXE02 if the register has been changed? In the ...
by om_tech_support_KR
Wed Jul 17, 2019 1:33 pm
Forum: Speed Control Systems
Topic: BMU Series, Clarifications
Replies: 4
Views: 1035

Re: BMU Series, Clarifications

Hi Mr.Thota, 1. Higher rated current circuit breakers are recommended because of inrush current at start up and when you start running the motor the current draw would be the max current spec given. You can use other circuit breakers that are closer to the max current draw but make sure they are slo...
by om_tech_support_KR
Tue Jul 16, 2019 1:51 pm
Forum: Stepper Motors and Controls
Topic: PK596-BE
Replies: 1
Views: 704

Re: PK596-BE

Hola Celestino10,

El motor PK596-BE era parte del paquete CSK596-NBTE esta seria la grafica del par velocidad de este paquete. El motor RK596BE era parte de la serie RK.
PK596.PNG
PK596.PNG (141.27 KiB) Viewed 562 times
CSK.PNG
CSK.PNG (80.19 KiB) Viewed 562 times
by om_tech_support_KR
Tue Jul 16, 2019 1:05 pm
Forum: Stepper Motors and Controls
Topic: Series RKII Driver
Replies: 1
Views: 652

Re: Series RKII Driver

Hola Celestino10, Desafortunadamente estos motores no van a ser compatibles con el driver RKSD507M-C. Este driver es solo compatible con los motores de la serie RKII por que tiene un voltaje mas alto que los anteriores. Quemaría las bobinas del motor por esta razón tienen conectores el motor y driver.
by om_tech_support_KR
Tue Jul 16, 2019 12:14 pm
Forum: Speed Control Systems
Topic: BMU Series, Clarifications
Replies: 4
Views: 1035

Re: BMU Series, Clarifications

Hi Mr.Thota, The circuit breaker we recommend is the Mitsubishi Electric Corporation NF30. This is referenced on page 12 of the manual I will link below. https://www.orientalmotor.com/products/pdfs/opmanuals/HM-5187-4E.pdf The X2 terminal is not mandatory to use. You would only need to use this if y...
by om_tech_support_KR
Tue Jul 09, 2019 11:29 am
Forum: Stepper Motors and Controls
Topic: Torque Setting & Limit Feedback
Replies: 5
Views: 1191

Re: Torque Setting & Limit Feedback

Hi Mr. Thota, You can set the torque limiting as a percentage on the MEXE02 software or with RS485 communication. To match it to the torque value you want to set you would have to reference the speed torque curve and look at the torque needed as a percentage at the specific speed. I will link the sp...
by om_tech_support_KR
Mon Jul 08, 2019 7:34 am
Forum: Stepper Motors and Controls
Topic: Using the AZD-KD stepper motor driver inputs and outputs
Replies: 1
Views: 669

Re: Using the AZD-KD stepper motor driver inputs and outputs

Hi Luther, With the AZD-KD driver you will only be able to read the internal I/O of the driver with the 007Dh register for inputs and 007Fh register for outputs. You can reference these registers on page 362 of the manual. You can change the I/O parameters the registers would be on page 419 and 420....
by om_tech_support_KR
Fri Jun 21, 2019 12:28 pm
Forum: Stepper Motors and Controls
Topic: CVK-SC Series Stepper Motor
Replies: 2
Views: 717

Re: CVK-SC Series Stepper Motor

Hi Mr.Thota, You are correct that driver would be the speed control driver where you can program 2 speeds a high speed and a low speed with the dials and switches on the driver. You would then choose the high or low speed with the I/O and the direction with the FWD or RVS input. The inputs can accep...
by om_tech_support_KR
Fri Jun 14, 2019 7:48 am
Forum: Stepper Motors and Controls
Topic: berger lahr and vexta
Replies: 3
Views: 962

Re: berger lahr and vexta

Hi eserv,

Thank you but unfortunately the driver was not manufactured by us. Looks like its manufactured by Toshiba you would have to contact them to verify the wiring configuration.
by om_tech_support_KR
Thu Jun 13, 2019 10:26 am
Forum: Stepper Motors and Controls
Topic: Torque Setting & Limit Feedback
Replies: 5
Views: 1191

Re: Torque Setting & Limit Feedback

Hi Mr.Thota, The AZ series has a torque limiting feature that you can set as a percentage and when it reaches that torque set it will turn on an output. The output that is turned on when the torque percentage set is reached is the TLC output. The part number would depend on the inertia needed from t...
by om_tech_support_KR
Thu Jun 13, 2019 8:33 am
Forum: Stepper Motors and Controls
Topic: berger lahr and vexta
Replies: 3
Views: 962

Re: berger lahr and vexta

Hi eserv,

Could you verify our driver part number? The PH533-A is one of our Japanese discontinued motors. I will link the spec sheet of that motor for your reference but it is only available in Japanese.