Search found 54 matches

by om_tech_support_KR
Thu Aug 22, 2019 12:46 pm
Forum: Stepper Motors and Controls
Topic: CVK Series, Radiation Protection
Replies: 2
Views: 218

Re: CVK Series, Radiation Protection

Hi Mr.Thota,

In regards to your inquiry unfortunately our products haven't been tested under these conditions. You would have to test them to verify if they will operate under these conditions.
by om_tech_support_KR
Tue Aug 13, 2019 6:34 am
Forum: Stepper Motors and Controls
Topic: CVK Series TIM & Alarm Output
Replies: 4
Views: 383

Re: CVK Series TIM & Alarm Output

Hi Mr.Thota,

From the wiring diagram the 24 VDC would go to pins 9 and 11. The pins 10 and 12 would go to 0 VDC. When using 24 VDC use a resistor 2.4 Kohm or larger to keep current at 10 mA or less.
by om_tech_support_KR
Tue Aug 06, 2019 11:23 am
Forum: Stepper Motors and Controls
Topic: CVK Series TIM & Alarm Output
Replies: 4
Views: 383

Re: CVK Series TIM & Alarm Output

Hi Mr.Thota, For the CVD228BR-K driver since they are open-collector type outputs you have to supply the 24 VDC voltage to the output to read that voltage when outputs are on. Reference page 8 of the link below for sample wiring diagram. You will have to use resistors to limit the current to less th...
by om_tech_support_KR
Tue Aug 06, 2019 11:13 am
Forum: Linear and Rotary Actuators and Controls
Topic: DRL Series Motorised Actuator
Replies: 1
Views: 266

Re: DRL Series Motorised Actuator

Hi Mr.Thota, The DRLII series is an open loop 5 phase motor so you will have to use a sensor for a defined home position. The DRS2 series would be a closed loop option with an absolute encoder as feedback but we don't offer one at the same frame size you were looking for. I will link them below for ...
by om_tech_support_KR
Wed Jul 24, 2019 8:31 am
Forum: Stepper Motors and Controls
Topic: Load with Stand while Power-off activated condition
Replies: 1
Views: 211

Re: Load with Stand while Power-off activated condition

Hi Mr.Thota,

The static friction torque given would be of the motor only without the gearhead. To get the total static friction torque of a geared motor you would multiply that value by the gear ratio. This would be the case for both of those electromagnetic brake motors.
by om_tech_support_KR
Mon Jul 22, 2019 1:37 pm
Forum: AC Motors
Topic: 2RK6RGN-CM encoder
Replies: 1
Views: 262

Re: 2RK6RGN-CM encoder

Hi Hawaiifairing,

The 2RK6RGN-CM feedback is tachogenerator not encoder. This speed control motor had a dedicated speed controller it will not be compatible with an Arduino.
by om_tech_support_KR
Thu Jul 18, 2019 1:27 pm
Forum: Stepper Motors and Controls
Topic: Unexplained exception for ReadWrite Multiple Registers (FC 17h)
Replies: 4
Views: 502

Re: Unexplained exception for ReadWrite Multiple Registers (FC 17h)

Hi dp1, After you get the exception do you get any alarms? Can you run the diagnosis function code 08h shown on page 270 to verify if getting the same response after you get the exception code. After you change register 1393h to 0 can you check in the MEXE02 if the register has been changed? In the ...
by om_tech_support_KR
Wed Jul 17, 2019 1:33 pm
Forum: Speed Control Systems
Topic: BMU Series, Clarifications
Replies: 4
Views: 574

Re: BMU Series, Clarifications

Hi Mr.Thota, 1. Higher rated current circuit breakers are recommended because of inrush current at start up and when you start running the motor the current draw would be the max current spec given. You can use other circuit breakers that are closer to the max current draw but make sure they are slo...
by om_tech_support_KR
Tue Jul 16, 2019 1:51 pm
Forum: Stepper Motors and Controls
Topic: PK596-BE
Replies: 1
Views: 447

Re: PK596-BE

Hola Celestino10,

El motor PK596-BE era parte del paquete CSK596-NBTE esta seria la grafica del par velocidad de este paquete. El motor RK596BE era parte de la serie RK.
PK596.PNG
PK596.PNG (141.27 KiB) Viewed 305 times
CSK.PNG
CSK.PNG (80.19 KiB) Viewed 305 times
by om_tech_support_KR
Tue Jul 16, 2019 1:05 pm
Forum: Stepper Motors and Controls
Topic: Series RKII Driver
Replies: 1
Views: 402

Re: Series RKII Driver

Hola Celestino10, Desafortunadamente estos motores no van a ser compatibles con el driver RKSD507M-C. Este driver es solo compatible con los motores de la serie RKII por que tiene un voltaje mas alto que los anteriores. Quemaría las bobinas del motor por esta razón tienen conectores el motor y driver.
by om_tech_support_KR
Tue Jul 16, 2019 12:14 pm
Forum: Speed Control Systems
Topic: BMU Series, Clarifications
Replies: 4
Views: 574

Re: BMU Series, Clarifications

Hi Mr.Thota, The circuit breaker we recommend is the Mitsubishi Electric Corporation NF30. This is referenced on page 12 of the manual I will link below. https://www.orientalmotor.com/products/pdfs/opmanuals/HM-5187-4E.pdf The X2 terminal is not mandatory to use. You would only need to use this if y...
by om_tech_support_KR
Tue Jul 09, 2019 11:29 am
Forum: Stepper Motors and Controls
Topic: Torque Setting & Limit Feedback
Replies: 5
Views: 773

Re: Torque Setting & Limit Feedback

Hi Mr. Thota, You can set the torque limiting as a percentage on the MEXE02 software or with RS485 communication. To match it to the torque value you want to set you would have to reference the speed torque curve and look at the torque needed as a percentage at the specific speed. I will link the sp...
by om_tech_support_KR
Mon Jul 08, 2019 7:34 am
Forum: Stepper Motors and Controls
Topic: Using the AZD-KD stepper motor driver inputs and outputs
Replies: 1
Views: 369

Re: Using the AZD-KD stepper motor driver inputs and outputs

Hi Luther, With the AZD-KD driver you will only be able to read the internal I/O of the driver with the 007Dh register for inputs and 007Fh register for outputs. You can reference these registers on page 362 of the manual. You can change the I/O parameters the registers would be on page 419 and 420....
by om_tech_support_KR
Fri Jun 21, 2019 12:28 pm
Forum: Stepper Motors and Controls
Topic: CVK-SC Series Stepper Motor
Replies: 2
Views: 442

Re: CVK-SC Series Stepper Motor

Hi Mr.Thota, You are correct that driver would be the speed control driver where you can program 2 speeds a high speed and a low speed with the dials and switches on the driver. You would then choose the high or low speed with the I/O and the direction with the FWD or RVS input. The inputs can accep...
by om_tech_support_KR
Fri Jun 14, 2019 7:48 am
Forum: Stepper Motors and Controls
Topic: berger lahr and vexta
Replies: 3
Views: 627

Re: berger lahr and vexta

Hi eserv,

Thank you but unfortunately the driver was not manufactured by us. Looks like its manufactured by Toshiba you would have to contact them to verify the wiring configuration.
by om_tech_support_KR
Thu Jun 13, 2019 10:26 am
Forum: Stepper Motors and Controls
Topic: Torque Setting & Limit Feedback
Replies: 5
Views: 773

Re: Torque Setting & Limit Feedback

Hi Mr.Thota, The AZ series has a torque limiting feature that you can set as a percentage and when it reaches that torque set it will turn on an output. The output that is turned on when the torque percentage set is reached is the TLC output. The part number would depend on the inertia needed from t...
by om_tech_support_KR
Thu Jun 13, 2019 8:33 am
Forum: Stepper Motors and Controls
Topic: berger lahr and vexta
Replies: 3
Views: 627

Re: berger lahr and vexta

Hi eserv,

Could you verify our driver part number? The PH533-A is one of our Japanese discontinued motors. I will link the spec sheet of that motor for your reference but it is only available in Japanese.

PH533-A.pdf
(650.11 KiB) Downloaded 46 times
by om_tech_support_KR
Fri May 31, 2019 11:34 am
Forum: Linear and Rotary Actuators and Controls
Topic: LAS Series, Rack and Pinion System
Replies: 1
Views: 524

Re: LAS Series, Rack and Pinion System

Hi Mr.Thota, Since this is a pulse input type driver first you would have to check the driver and controller are both set to same pulse input mode. If both are using the same pulse mode 1 pulse or 2 pulse mode then you can check the wiring is correct. I will link the manual for your reference. HL-80...
by om_tech_support_KR
Fri May 31, 2019 11:26 am
Forum: AC Motors
Topic: problem to control Ac motor using a relay
Replies: 1
Views: 585

Re: problem to control Ac motor using a relay

Hi Walid, In regards to your post, we are product experts on the components that we manufacture and unfortunately, we do not have experience with this type of circuits. Therefore, we are unable to provide further insight than what you have determined. For something like this, I would recommend that ...
by om_tech_support_KR
Thu May 23, 2019 8:17 am
Forum: Stepper Motors and Controls
Topic: Azd-KD Modbus via FX5U
Replies: 1
Views: 527

Re: Azd-KD Modbus via FX5U

Hi Art38,

Could you send me the query you are sending when you try to read? Also can you try the example read query shown on page 268 of the manual.

https://www.orientalmotor.com/products/ ... 262-6E.pdf
by om_tech_support_KR
Thu May 23, 2019 8:03 am
Forum: Stepper Motors and Controls
Topic: AZM66AC with AZD-AD driver position control Modbus
Replies: 1
Views: 476

Re: AZM66AC with AZD-AD driver position control Modbus

Hi Adeel, If you are only using the continuous forward and backwards commands they will keep running until you write a 0 to the 007Dh register to stop them. To run a positioning point you will have to use the M0-M7 inputs and the START bit. We have an example on how to set a position and run it star...
by om_tech_support_KR
Wed May 22, 2019 1:38 pm
Forum: Stepper Motors and Controls
Topic: Meaning of each bit of the Information Record?
Replies: 3
Views: 671

Re: Meaning of each bit of the Information Record?

Hi dp1, For the Information Record they are the last 16 information pieces saved in the RAM in order from latest to oldest. For the list of them reference page 469. If you would like to read the INFO parameters you can reference the registers starting on page 409. https://www.orientalmotor.com/produ...
by om_tech_support_KR
Thu May 09, 2019 10:53 am
Forum: Stepper Motors and Controls
Topic: 3 Drivers MODBUS RS485 ERROR#84
Replies: 1
Views: 530

Re: 3 Drivers MODBUS RS485 ERROR#84

Hi otter_plc,

Have you tested each cable individually or turning of power to axis 1 and 2 or 3 to test axis 2 and 3 individually?
Also when you mention you send commands and you get a response / movement is this to only one axis or when the 3 axis are turned on?
by om_tech_support_KR
Tue May 07, 2019 10:21 am
Forum: Stepper Motors and Controls
Topic: Sporadic RS485 MODbus communication failure
Replies: 2
Views: 595

Re: Sporadic RS485 MODbus communication failure

Hi Dominique, Since this looks to be happening when you switch writing between the 2 axis could be there isn't enough delay between the 2 messages sent. I would try adding a longer delay between them. Also you can do an alarm reset to reset the 84h alarm code this is a RS-485 communication error so ...