speed control using modbus for BLV

ADITJH
Posts: 1
Joined: Mon Jul 24, 2017 6:40 pm

speed control using modbus for BLV

Postby ADITJH » Mon Jul 24, 2017 6:50 pm

hi ,i'm using oriental blvd20km

is there other way to control speed than using operation data ?

best regard

om_tech_support_JS
Posts: 166
Joined: Tue May 10, 2016 4:48 pm

Re: speed control using modbus for BLV

Postby om_tech_support_JS » Tue Jul 25, 2017 9:20 am

Hi ADITJH,

The BLVD20KM speed controller can have the speed set via the internal potentiometer, external potentiometer, or external DC voltage. If you use the OPX-2A control module, then you would also be able to set a digital setting for the speed. Alternatively, this speed controller option allows you to control the product through Modbus (RS-485 Communication).

Was there a speed setting method that you were interested in using? Are you looking to utilize the Modbus communication? If so, I have linked a manual below for this option:
http://www.orientalmotor.com/products/p ... 114-2E.pdf


In referencing the manual, page 6 walks through the initial setup. Page 19 shows the use of the input command register (007Dh) and page 25 shows the registers for the operating speeds.


Return to “Speed Control Systems”

Who is online

Users browsing this forum: No registered users and 1 guest