Q: Hi, I'm using your BLE speed control motor and driver system for a conveyor that I'm building. I wish to program speeds for all 8 data sets digitally with your OPX-2A programming module, then use I/O from a PLC to run the motor at those programmed speeds. However, I can't seem to make data 0 or data 1 work with digital speeds that I have already programmed. Data 0 or data 1 seem to only respond to internal potentiometer and external potentiometer's analog inputs. How can I make this work?

A: You'll have to change a setting within the BLE driver with the OPX-2A programming module to enable this type of operation. You'll have to change the setting for the SYS-0-04 from its initial/default value of 1 to 0. Once you do this, it will disable the analog inputs on the driver and enable digital speed settings from data 0 to data 7 instead. Please see below for an excerpt from the BLE manual:

BLE OPX-2A SYS-0-04 digital, analog input setting.jpg
BLE OPX-2A SYS-0-04 digital, analog input setting.jpg (224.36 KiB) Viewed 3677 times

You can also change this setting with the MEXE02 GUI software. Please see below:

BLE MEXE02 digital, analog input setting.jpg
BLE MEXE02 digital, analog input setting.jpg (113.36 KiB) Viewed 3677 times


REFERENCE MATERIAL:
BLE, OPX-2A MANUAL: http://www.orientalmotor.com/products/p ... -5042E.pdf
BLE, MEXE02 MANUAL: http://www.orientalmotor.com/products/p ... -5046E.pdf

Return to “Speed Control Systems”

Who is online

Users browsing this forum: No registered users and 1 guest