I'm having a motor issue. I will try to give all the info possible.

motor:
3 hp
208 - 230 V
three "butt" connectors at the motor (red, black and blue)
https://catalog.orientalmotor.com/item/ ... 0n5-mv9awn

vfd:
3 hp
208 - 230 V
https://www.valinonline.com/products/esv222n02yxb

It's starting up for 3-4 seconds and right after that it trips the 30 amp breaker. It's on its own circuit (alone) with 10-2 nmd90 wire (90 feet long) with a 30 amp breaker.

Any idea what it could be?

om_tech_support_KR
Posts: 69
Joined: Thu Jan 11, 2018 3:03 pm

Re: Electric motor issue

Post by om_tech_support_KR » Wed Jan 16, 2019 8:42 am

Hi Luke,

For induction motors we recommend using slow blow type fuses because the inrush current on start up of these motors on average is 3-5 times the full load current.