Azd-KD Modbus via FX5U

Post by Art38 » Wed May 22, 2019 9:51 pm

Hello

I use PLC MITSUBISHI FX5U for control Azd-KD motor. Now i can control motor(Change position data ,Jog ,Home) via modbus (10H) Holding register.
But i have problem about can't reading register(03H).I try with other address but not response from AZD-KD. PLC and Servo no error.
Thanks
79570.jpg
79570.jpg (134.95 KiB) Viewed 624 times

om_tech_support_KR
Posts: 59
Joined: Thu Jan 11, 2018 3:03 pm

Re: Azd-KD Modbus via FX5U

Post by om_tech_support_KR » Thu May 23, 2019 8:17 am

Hi Art38,

Could you send me the query you are sending when you try to read? Also can you try the example read query shown on page 268 of the manual.

https://www.orientalmotor.com/products/ ... 262-6E.pdf